As you install in in - and Out header the probes of dP meters/ pressure gauges it's on per side enough as the hydraulic pressure will be the same as there is not so much difference in piping structure of ea. pressure vessel. It's hydraulic law that the pressure will be the same.Same is for pump stations. From my point of view this is coming for the PID of one pump station/ filter station and then  copy and paste for the system. You can use also on pressure transmitter in Inlet and one in outlet the difference is calculated by the Control system. Therefore you have 3 data Inlet pressure, outlet pressure and calculated difference pressure. Saves Money.

Best regards Dieter